  • Nov 13, 2006, 10:00 AM
    Matt Kaleida
    Electric Coleman Mobile home furnace
    The blower fan keeps running and will stop until the breaker is shut off for a while. It may run fine through its complete cycles for a day or two, but will do it again! The furnace hasn't been used for about 4 years. What needs fixed or replaced, and where do I find these parts? The trailer was built in 1974, is in fair shape, and located in Summersville, West Virginia. Help!
  • Nov 13, 2006, 11:15 AM
    labman
    In something that old, the blower is controlled by a relay operated by a limit switch. Follow the lead from the motor back to a little box. It should have 4 wires, the one from the motor, one from the house wiring, one to the transformer, and one to the limit switch. If, with the power off, the line from the house and the lead to the motor have continuity, the relay is stuck. Take it to a electrical or HVAC supply, and let them match it. They should have at least a work alike. If it is open with the power off, them likely it is the limit switch. Follow its wire into the heat exchanger, and take it to the supply house. The older systems are cheaper and easier to fix.
  • Nov 22, 2006, 04:35 AM
    hvac1000
    The parts may not be available. Have an HVAC person change the system over to a Sequencer and get rid of all the old obsolete relays Etc.
  • Feb 13, 2007, 09:10 AM
    dusty1954
    Ihave a coleman electric furnace model #3500A818 the coils light up even when the thermostat is in the off position
  • Feb 13, 2007, 09:25 AM
    hvac1000
    1 Attachment(s)
    Quote:

    Originally Posted by dusty1954
    Ihave a coleman electric furnace modle #3500A818 the coils light up even when the thermostat is in the off position

    Bad sequencer

    Part number 3115-3571 Sequencer

    Sequencer controls the sequence in which the heating elements & blowers turn on. This one has the ability to control up to 2 blowers (H1-H4) and 3 heating elements (M1-M6). Replaces 3400-357,
  • Sep 24, 2013, 08:41 PM
    baer1213
    I have a coleman furnace model 7655-856 think it a 1982 when it call for heat it light up but blower don't kick on .I cheeked blower motor and it run. What do I need to replace
  • Sep 25, 2013, 04:55 PM
    Grady White
    baer1213: I suspect you have a bad fan switch. This is a temperature actuated switch which closes to turn the fan on once a certain temperature at the switch is reached.