  • Dec 9, 2009, 04:23 PM
    lanna0547
    Furnace blowing air but not sufficient to heat the house
    We recently had to replace the blower motor, fan, and capacitor in our furnace. The furnace is blowing air but not sufficient to actually heat the house. Any suggestions on what this new problem maybe?
  • Dec 9, 2009, 04:38 PM
    lanna0547

    It is Heil Quaker (sub of Whirlpool). Model number: NUGJ100F01
  • Dec 9, 2009, 08:29 PM
    KC13

    Is the blower running backward? You may have to open access panel to view rotation. If motor is reversible, it may have been set incorrectly during installation.
  • Dec 10, 2009, 10:22 AM
    lanna0547

    That was the problem. Thank you very much!!