    Curier heater acting up
    My 12 yr. od heat and air currier 8000 weather maker is acting up. The main blower(lower)
    Will come on, then the top little one, the ignition gets red hot but then it will shut down and restart. Some times the propane will just ignite then shut down again. I found that if I pulled one way or the other on the upper wires, of the panel where all the wires join,(control panel) it will work fine. I haven't 180ed the panel to check out the other side yet.
    Short maybe?
    Thanks, tim
  • Nov 13, 2006, 07:02 PM
    ptsn1
    Quote:

    Originally Posted by ptsn1
    my 12 yr. od heat and air currier 8000 weather maker is acting up. the main blower(lower)
    will come on, then the top lil one, the ignition gets red hot but then it will shut down and restart. some times the propane will just ignite then shut down again. i found that if i pulled one way or the other on the upper wires, of the panel where all the wires join,(control panel) it will work fine. i havent 180ed the panel to check out the other side yet.
    short maybe?
    thanx, tim

    I get a code #31
    Pressure, draft safeguard, or auxiliary limit(when used) switch did not close or reopened.
    Check for
    -defective inducer motor or starter capacitor
    -defective pressure switch or connection
    -low inducer voltage
  • Nov 13, 2006, 10:29 PM
    NorthernHeat
    Also check for blocked fresh air and flues, birds nest, wasp nests, plugged pressure switch vacuum ports.