  • Dec 7, 2009, 10:01 AM
    breakersjl
    Can culter hammer breakers be used in a GE panel or is this against code?
    Can culter hammer breakers be used in a GE panel or must GE breakers be installed? I was told installing CH breakers in a GE panel is against code?
  • Dec 7, 2009, 12:25 PM
    tkrussell
    Check the instructions or datasheet for the CH breaker. Most likely not able to use in GE panels due to UL Listing. There are a few breakers that are UL Listed to work in other panels.
  • Dec 7, 2009, 05:22 PM
    Tev

    Cutler-Hammer does have breakers that are UL certified to fit 6 other manufacturer's panels. GE is one of them. The only way to know if you can use a different manufacturer's breaker is to do the research.

    The person that told you installing a CH breaker in a GE panel was against code made a general statement that is false. Here is a link to the CH classified replacement breaker information page if he doesn't believe you. Link
  • Dec 8, 2009, 05:32 AM
    tkrussell

    Keep in mind, only the Cutler Hammer Type CL and CHQ are listed as replacement breakers allowed in other panels.

    Not the standard and popular Type BR or CH.