I just installed a concord 80,000 95% furnace, now I am getting a blinking light 3 times, if I jump the pressure sensor wires it works fine what are my possible problems
![]() |
I just installed a concord 80,000 95% furnace, now I am getting a blinking light 3 times, if I jump the pressure sensor wires it works fine what are my possible problems
Try BRIEFLY disconnecting the exhaust vent, see if unit will advance through operating sequence. If it does, vent is restricted or undersized. Check for trapped condensate in vent, correct pitch if necessary.