Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Electrical baffle (https://www.askmehelpdesk.com/showthread.php?t=419342)

  • Nov 25, 2009, 02:37 PM
    reeddean98
    Electrical baffle
    I have come across a sub panel/ 50 amp/ 220 .It is for a garage, very small. When I put the tester on the legs, (leg to ground, 110/ other leg to ground, 110, both together, 220) everty thing seems normal. but, I wired plugs off a 20 amp breaker from this box and they are showing me I have 110, but they will not work?I checked from plug, hot to neutral, 110, and hot to ground, 110? I am lost? Any help?
  • Nov 25, 2009, 02:48 PM
    tkrussell
    You have a tandem breaker, two separate poles or switches, that plug into a full size breaker slot, and it is plugged into only one bus tab. These need to span both legs or bus of a panel, always.

    Getting it into the right position will produce 240 volts across the two terminals.
  • Nov 25, 2009, 03:00 PM
    reeddean98
    Quote:

    Originally Posted by tkrussell View Post
    You have a tandem breaker, two separate poles or switches, that plug into a full size breaker slot, and it is plugged into only one bus tab. These need to span both legs or bus of a panel, always.

    Getting it into the right position will produce 240 volts across the two terminals.

    I have achieved 220 volts and 110, my problem is the plugs are showing me 110, but I am getting no power?
  • Nov 26, 2009, 01:40 AM
    thayden88

    I've recently seen a similar problem, try checking all your neutral connections. I was reading around 110v but nothing worked. I believe the solution was a loose neutral.