    paildog
    Rheem pilot stay lit but wong ignite gas in the chambers
    Rheem model rgld-1one-jr, ignitor model sp715-us17-15u. The pilot will stay lite but will not lite the gas in the gas chambers. Yesterday I turned everything off all night gas valve and t-stat when I got up ithought I would turn it on and listen for a while. So the pilot lights and the gas was supplied to the chamber for about 2 seconds and went off pilot still on waited gas was supplied to the chamber about 10 seconds later stayed on for about 6 seconds and the went off . But thi pilot stayed on but nothing elsr happened so I turned everything off and went to work. Got home pilot will ignite but nothing was supplied to chambers. Any help would be grateful.
  • Nov 24, 2009, 04:11 AM
    hvac1000
    Is voltage getting to the gas valve during the cycle.
  • Nov 24, 2009, 06:14 PM
    paildog

    There four wire going to the gas valve how do I no what ones to meter
  • Nov 24, 2009, 06:19 PM
    paildog
    There are 2 black wires 1 yellow 1gray and 1 orange
  • Nov 24, 2009, 10:21 PM
    paildog

    I don't have an ohm meter but I do have ameter that reads volt. So I put the ground on the meter to ground and the other to the lead to the white wire that has a p under which I am keading that means power . That is the only one I got voltage on and yes it was 24 volts.
  • Nov 24, 2009, 10:23 PM
    paildog
    And there was no gray wire it was white
  • Nov 25, 2009, 04:09 AM
    KC13
    2 Attachment(s)
    Do these look familiar? Sounds like a faulty ignition module (pic 2).
  • Dec 1, 2009, 10:34 PM
    paildog
    Yes that is my furnace. And I did a couple of test on the gas valve put a jumper from p to m and the burners ignited so I rulled out the gave valve and yes you were correct that is was the ignition control unit. I would like to thank you for the time you spent answering my question. It is nice to now there are people like you that are willing to help. Again thank you very much for your time.
  • Dec 1, 2009, 11:46 PM
    hvac1000
    KC13 is a good guy with a lot of field experience and helps many people here. I am just glad you got it going.