-   -   Nordyne blower motor will not start with a call to heat when set on auto. (https://www.askmehelpdesk.com/showthread.php?t=418270)

  • Nov 22, 2009, 07:53 AM
    antboggie1
    Nordyne blower motor will not start with a call to heat when set on auto.
    I have a nordyne eletric furnace , my blower motor will not start when set on auto with a call to heat. The elements will heat up but the motor will make humming sound and will start if I push wheel with my hand.I have checked the motor it is fine .
  • Nov 22, 2009, 09:06 AM
    Joshdta

    Does it start and run with the fan set to on?
  • Nov 22, 2009, 09:17 AM
    antboggie1
    Yes
  • Nov 22, 2009, 12:09 PM
    KC13
    Quote:

    Originally Posted by antboggie1 View Post
    The motor will make humming sound and will start if i push wheel with my hand. I have checked the motor it is fine .

    Umm, sounds like you just checked the motor and it isn't fine at all... the run capacitor may be the culprit. Does the motor become overheated (too hot to touch - use care) when operated for a while?
  • Nov 22, 2009, 12:23 PM
    antboggie1

    No ,motor not over heating at all
  • Nov 22, 2009, 12:31 PM
    KC13
    If the motor runs with a push, it is being powered. Turn off power to unit, and check electrical connections to motor and capacitor. If good, capacitor check and/or replacement would be the most economical next step.
  • Nov 22, 2009, 12:31 PM
    antboggie1

    Post of the capacitor is rusted due to water from the ac leaking on it,could this be the problem ?
  • Nov 22, 2009, 12:37 PM
    KC13
    Definitely. Clean up connection as much as possible, see if blower will start on its own.
  • Nov 22, 2009, 12:37 PM
    antboggie1

    Thank you, I will give it a try.