While doing some electrical work the other day I noticed that on a circuit had 120v across the neutral and the neutral buss which it was at the time disconnected from. I immediately assumed dead short but there had never been a problem with the circuit breaker tripping. I was perplexed also because if I reconnected the neutral to the buss I assumed it would energize all the neutrals in the box and create both a short to ground back at the main breaker box where neutral and ground are connected and also create a 0v difference between all the hots and neutrals allowing no current to flow and nothing to function. Obviously neither of these things happened but I left the circuit off for the night and had an electrician friend look at it the next day. He found nothing wrong and told me I was getting the 120v from neutral to neutral buss because of a motor that was on in the circuit and by connecting the two contacts with my multimeter probe I was completing the circuit. This again perplexed me as I did not think checking voltage passed any current through the multimeter and if enough did to power a motor I thought it would destroy the multimeter.
So my question is this: First off shouldn't there be a voltage drop between the hot and neutral side of a motor? I thought there should be 120v on one side and 0v on the other. If there is no voltage drop wouldn't that be a short to ground? I know induction loads do not behave the same way as resistive loads do but I thought the basics were the same. Any insight would be greatly appreciated. Thank you.