#12 AWG copper wire for baseboard heaters
I want to run a circuit for baseboard heaters and have been told to use #12 AWG copper. I have a total of three heaters in separate rooms each controlled by its own thermostat. I would like to use #14 AWG copper and have calculated the voltage drop with #14 to be less than 1% with all three heaters on together. Is there a reason why I shouldn't use #14? The code recommends no more than a 3% voltage drop, lists the ampacity of #14 as 20 amps, and allows a circuit breaker of 15 amps. The heater manufacturer recommends an 80% derating. It seems that #14 complies with all of these. Am I missing something?