  • Nov 14, 2009, 11:47 AM
    bubbashasta
    Electric Furnace
    I have an lennox electric furnace the low volt is disconnected and need to re wire in the furnace I have yellow not designated, black labeled "G" blue labeled "R" red labeled "W-1" orange labeled "W-2. Two wires at the thermostat red-white
  • Nov 14, 2009, 12:07 PM
    KC13

    If you are wiring this for heating-only, and you only have 2 wires to the thermostat, connect one to "R" and the other to "W1" and "W2". Insulate or cap the remaining 2 wires, then test the operation. If the electric heaters turn on but the blower does not, add the "G" wire to the "W1/W2" junction.