  • Nov 6, 2009, 02:58 PM
    tpack37
    Concord 80 plus problems
    Hi I have a concord 80 plus furnace that's blowing nothing but cold air. Also I noticed that the ignition coil or rod does glow and because it doesn't glow it not igniting the gas in the furnace. The green light blinks 4 times which based on the codes on the door means the limit or roll out switch is open. How can I fix this without having to call a HVAC peson. Thxs
  • Nov 6, 2009, 03:44 PM
    Joshdta

    The ignitor does or does not glow? Change you filter and check the high limit switch, just tap it. Also there are probably 2 roll out switches follow the red wires the roleouts have red reset buttons in between the wires.
  • Nov 6, 2009, 03:59 PM
    tpack37
    Thanks for the answer. Where is the high limit switch and the roll out switch located?
  • Nov 6, 2009, 04:01 PM
    Joshdta

    Roleouts are usually on top or on either side of the burner
    http://www.mobilehomerepair.com/medi...yne/626343.jpg
  • Nov 6, 2009, 04:02 PM
    Joshdta
    High imit above the burner.

    http://store.hamiltonhomeproducts.co...-29041-005.jpg
  • Nov 6, 2009, 04:10 PM
    tpack37

    OK thanks. Ill check both and let you know what happens
  • Dec 15, 2013, 07:45 AM
    ken1966
    Had power surge and furnace wouldn't ignite ran new electrical wiring to stop further surges and furnace quit working all together so relaced ingniter control board and still get nothing
  • Dec 15, 2013, 08:53 PM
    Grady White
    May be a silly question, maybe not but do you have 120 volts between the black & white wires coming into the furnace? Is the ground connected?