Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   58STA110 Carrier furnace not igniting (https://www.askmehelpdesk.com/showthread.php?t=413293)

  • Nov 6, 2009, 08:40 AM
    NOVATreker
    58STA110 Carrier furnace not igniting
    Hi all,

    I have a 58STA110 Carrier furnace manufactured in Oct of 02 that is not igniting. Cooling is fine. The induction fan starts and runs for a few seconds. I hear and smell the gas start blowing, but after a few seconds the gas shuts off followed by the fan cutting of several seconds later. The flame never ignites. The service light is showing an error code 14.

    Any ideas?
  • Nov 6, 2009, 10:01 AM
    KC13
    Did you ever observe the glow from the hot surface ignitor? If not, it has failed or is not being powered by the circuit board.
  • Nov 7, 2009, 09:25 AM
    NOVATreker

    I found the problem... The previous owner removed the hot surface ignitor. That would definaly cause a failure.
  • Nov 7, 2009, 10:39 AM
    KC13
    Seek out part # LH33ZS004. Treat it like an egg, and don't touch the element with your bare hands.