    Intertherm/Nordyne furnace - not igniting
    I have a 20-yr old furnace (old model# G6 RC080C). No blue flame through the burner view port, so assume that the ignitor is bad. There are no issues with gas supply. Is it simply a matter of getting an ignitor kit and replacing the old one? Or is there a possible issue with the control board?
  • Oct 28, 2009, 05:43 AM
    hvac1000
    Test to see if voltage is getting to the ignitor when there is a call for heat.
  • Oct 29, 2009, 03:00 AM
    madeelad

    Thanks hvac1000. I will need a special device to check electrical flow, right? I assume there are two leads of some kind which need to be connected at different points to see if the voltage is getting to the ignitor?
  • Oct 29, 2009, 06:38 AM
    hvac1000
    If you are going to work on HVAC equipment a minimal set of testing tools are necessary and the Skill in the knowledge of how to use them properly.