Carrier lp gas pack 48gp repeat rollout switch lockouts
Unit is around 4 years old and has been a repeat offender with rollout sw trips, soot build-up and sometimes foul smelling exhuast since the second year. Unit belongs to friend who is fed up with the dealer installer due to no resolve. I have disassembled burner,cleaned out soot (alot) from chamber,physically inspected chamber no apperant cracks, checked for correct orfice size,replaced rollout switch with correct replacement (it had cycled so many times it was shot). Reassembled and measured gas pressure 11"wc on outlet of gas valve to burner. Unit flame looks great.my thought now is that this 11" wc is what I should have at the inlet of the vavle and should be actually less on outlet if valve is working correctly? I'm confused can somebody help me or is this unit a lemon?