  • Oct 25, 2009, 09:15 PM
    Geoat
    How do I connect 3 240v blower heaters?
    How do I connect 3 240 v blower heaters (each heater with wall thermostat is in its own room) in a single circuit?
  • Oct 26, 2009, 03:17 AM
    stanfortyman
    I would run the feed to the first thermo and then daisy chain on to the other two.
    The run a switch leg to each heater from the thermostat.

    What size are these heaters? Will the all fit on one 20A circuit? If so use 12/2 for everything.

    #10 will overload boxes real fast if you have to bump it up to a 30A circuit, which is legal for this circuit.
  • Oct 31, 2009, 07:55 PM
    Geoat
    Connecting single pole thermostats
    How do I connect single pole thermostats to operate blower type heaters. The wire from panel is 12-2 and is daisy-chained as you suggested. There are 3 heaters in the circuit.
  • Nov 9, 2009, 10:30 PM
    Geoat
    Connecting single-pole thermostats to 3 blower heaters in 1 circuit
    Daisy-chained the line from panel and put in individual lines to each heater as you suggested.

    How do I wire the thermostats and carry power on to the next... Using 12-2 wire.