    New heat pump with old smaller air handler
    I had a 10 seer heat pump that was replace with a 13 seer heat pump. The air handler or coil was not change it is a 10 seer. My problem is I have 1039 sq ft. my den and bedroom are the farest away from air handler the den has no air flow and bedroom has very little. What is the problem.
  • Oct 25, 2009, 01:36 PM
    hvac1000
    3 Attachment(s)
    The actual problem is hard to say. Dirty air filters, dirty original indoor coil, improper duct connections or the coil inside might be icing up due to the mis-matched indoor coil.

    If the indoor coil does not have a thermostatic expansion valve installed and you run a 10 SEER coil with a 13 SEER outside unit major problems can and do occur.

    A 13 SEER outside heat pump should never be installed with an old 10 SEER coil. You might be able to get away with it on a strait A/C system but not on a heat pump. Whoever installed your new outside unit did you a great injustice and I suggest you call them back to do the job correctly.

    Here are a few files on the subject of mis-matching new outside units to old coils.