  • Oct 24, 2009, 01:34 PM
    dsmall
    No gas to the furnace
    Carrier Crusader Gas furnace 19 years old
    Will not flame up when the glow plug lights up. Technician just left $75 to tell me I need a new circuit board #CES0110057-00 and $350.00
    My question is is that a fair price and do you believe I need a new board.

    David
  • Oct 28, 2009, 06:23 PM
    scooterVA23692

    I have the same problem. I have a Carrier 58RAV055-GC with circuit board CEES0110057-00. So far I see the board for sale on the internet at various locations for $170 to $230. I tested my gas valve and the various safety switches and everything looks good so far.-but the gas valve never gets the signal to turn on after the 'glow plug' lights up. I suspect it is the board.
  • Oct 28, 2009, 06:28 PM
    scooterVA23692

    FYI: I see that there is a Nov.2007 post by 'DWF' that writes about the same kind of problem. The response was that the board is bad.
  • Oct 28, 2009, 09:37 PM
    hvacservicetech_07

    It is very possible that the circuit board is bad, the only way to know for sure is with a voltage meter. That price seems kind of high.
  • Oct 29, 2009, 09:06 AM
    dsmall
    Replaced the circuit board ($175) and it works fine. Thanks for the response.
  • Nov 4, 2009, 08:47 AM
    scooterVA23692

    FYI: I replaced the circuit board on mine also ($177 w/shipping) and now it works fine. Thanks for the input.