  • Oct 23, 2009, 07:58 AM
    essuo
    Installing a new 24V Honeywell AT72D transformer
    The old transformer had 4 wires different colors. New Honeywell AT72D has Primary BLK-COM, WHT-120V 50/60Hz, and two screws on the load side with an R and C. I thought it would be obvious, but it is not to me. Do I have it right? PR1-BLK, PR2-WHT Secondary I am not sure which should go where? SEC1/SEC2 R or C?

    Thanks
  • Oct 23, 2009, 08:20 AM
    KISS

    Here is the installinstructions:

    http://customer.honeywell.com/techli...0s/60-0428.pdf

    You failed to say what colors the old transformer had. If it had a white and a black connected to the primary side, white and black are appropriate.

    The red and orange wires should each have a wirenut placed on the ends (capped).

    The secondary phasing only matters with newer furnaces with flame rectification flame proving systems. In which case, an error code will be set on the control board. No damage will result.
  • Oct 23, 2009, 09:11 AM
    essuo

    Primary colors on the old were Black - PR1 and White PR2 and Secondary colors were Red for SEC-1 and Blue for SEC-2 My furnace is at least 20 years old, so it should not matter where SEC wires go. Thanks for your answer.
  • Oct 23, 2009, 09:45 AM
    KISS

    Yep.