  • Oct 22, 2009, 01:12 PM
    lvania
    Minimum rigid conduit size
    What is the minimum conduit size for 3 -#2 copper wires to a service panel?
  • Oct 22, 2009, 01:26 PM
    tkrussell
    Always needs to know the insulation, as different types have different outside dimensions.

    Assuming THHN/THWN insulation, 1 inch is the minimum.

    Electricians never use 1 in GRC for 3 #2 wires. We will always use a min of 1-1/4".

    Just the way we are.
  • Oct 22, 2009, 01:47 PM
    KISS

    Might you need 4 wires. L1, L2, G and N?