What is the minimum conduit size for 3 -#2 copper wires to a service panel?
![]() |
What is the minimum conduit size for 3 -#2 copper wires to a service panel?
Always needs to know the insulation, as different types have different outside dimensions.
Assuming THHN/THWN insulation, 1 inch is the minimum.
Electricians never use 1 in GRC for 3 #2 wires. We will always use a min of 1-1/4".
Just the way we are.
Might you need 4 wires. L1, L2, G and N?