  • Nov 4, 2006, 06:29 PM
    steve3656
    Honeywell Rth7000 Thermostat
    I just bought a honeywell rth7000 thermostat, i am installing in a old house that only uses 2 wires, one is green and the other brown, can anyone advise me how to connect these 2 wires to this unit i am not sure exactly where to connect them to on the honeywell thermostat--thanks
  • Nov 4, 2006, 07:00 PM
    labman
    If it will work with only 2 wires, connect one to the RH, and the other to the W. It might be best if you checked to see which one connected to the R terminal at the furnace or directly to the transformer and made it the one connected to RH. See
    https://www.askmehelpdesk.com/heatin...ons-40771.html

    It may need batteries for power.
  • Nov 4, 2006, 07:44 PM
    steve3656
    Labman thanks for your reply, there is no RH on the RTH7000, its labeled C, G, Y, W, RC, R, PLEASE ADVISE
  • Nov 4, 2006, 08:14 PM
    labman
    OK the red wire goes to R. If you have A/C, but only one transformer, jumper R to RC.
  • Nov 4, 2006, 09:22 PM
    steve3656
    I don't have a/c its just a oil burner, so are you saying that I should connect the Green(ground wire) to C and the brown(hot wire) to R, then should I remove the jumper that connects Rc to R?
  • Nov 5, 2006, 01:54 PM
    NorthernHeat
    Quote:

    Originally Posted by steve3656
    I dont have a/c its just a oil burner, so are you saying that I should connect the Green(ground wire) to C and the brown(hot wire) to R, then should I remove the jumper that connects Rc to R?

    Just connect one wire to R it doesn't matter if jumper is there for R-Rc or not. The other wire goes to W.