Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Fireplace mainburner doesn't light (https://www.askmehelpdesk.com/showthread.php?t=408315)

  • Oct 21, 2009, 10:02 AM
    dannykan
    Fireplace mainburner doesn't light
    Hi,

    I have a millivolt Honeywell gas control system for my fireplace. The pilot is on.
    The thermopile voltage on the terminals is 663 mV. I checked the burner orifice and it is OK. When I command the mainburner to come on, nothing happens.
    Would please advise how to proceed.

    Regards,
  • Oct 21, 2009, 10:11 AM
    hvac1000
    Some fireplaced also have a thermocouple besides having a thermopile. If so it is possible the thermocouple is defective.
  • Nov 6, 2009, 09:58 AM
    dannykan
    Quote:

    Originally Posted by hvac1000 View Post
    Some fireplaced also have a thermocouple besides having a thermopile. If so it is possible the thermocouple is defective.

    I have replaced the thermocouple and cleaned up the thermopile. I am now reading 773 mv.
    The main flame is still not coming on!
    Valve info: Honeywell millivolt Gas valve; VS8420E or 82L8601
  • Nov 6, 2009, 06:11 PM
    hvac1000
    2 Attachment(s)
    Check to see if that milivoltage is getting to the gas valve. If it is and the valve is not opening then I would suspect the valve. This might not be your fireplace setup exactly but the two items below might help.