  • Oct 18, 2009, 06:25 PM
    rdzierniejko
    Honeywell Focus Pro 6000 (Heat and A/C reversed)
    I recently purchased a loft. The unit had an existing "Mammoth -- Water Source Heat Pump" thermostat. I purchased a Honeywell Focus Pro 6000 to replace this. I have hooked up the new thermostat, but the heat and A/C are reversed. In other words, to get the heat working, I need to set the system to "cool". Instead of blowing cold air, it blows heat. What am I doing wrong? Thanks.
  • Oct 18, 2009, 06:42 PM
    KISS

    Page 11 of your manual setup function #2. Change to the other value. Default is 0. Chage to 1 if 0; Change to 0 if 1.
  • Oct 19, 2009, 08:44 AM
    rdzierniejko
    Worked perfectly. Thanks.