  • Oct 15, 2009, 05:52 PM
    jcapone2524
    Bleeding hrdronic boiler
    I have a hydronic gas fired boiler I am trying to service this boiler has been off for at least one season that I know off I ran system return side was not returning properly so I started bleeding system shutting off valve before circulator pump connecting hose to above spikit and started draining but very little to none water came out I manually ran water threw system to push air out but only received a little more of water flow I ran for at least 30 min still cannot get proper return do anybody know how I can bleed this system problem properly
  • Oct 15, 2009, 06:13 PM
    T-Top
    Did you check to make sure the pump was running and that the impeller was not restricted with settlement? No air bleeder at the coil or coils?
  • Oct 15, 2009, 06:20 PM
    jcapone2524

    I didn't check pump or for coils yet I don't get it I'm forcing water threw system and only getting little water back when I should be pushing out air
  • Oct 15, 2009, 06:26 PM
    T-Top
    You got a bad restriction. You need to flush backwards through the system if you can to get it cleaned out.
  • Oct 15, 2009, 06:30 PM
    jcapone2524

    How cause this boiler doesn't have a valve after expansion tank to connect hose too
  • Oct 15, 2009, 06:57 PM
    T-Top
    That's a question for the person who installed it. Can the system be backed flushed? Your going to need to break the system down to find the restriction if not.
  • Oct 15, 2009, 08:39 PM
    hvac1000
    If the system has zone valves they have to be open to perform a flush OR fill the boiler system. Most zone valves have a manual lever or setting to allow this with power off.