I recently hooked up a hot tub that required a 240v with no neutral. (50A) I took a two pole 60 from the main service and ran 6/3 teck cable to a 2cct outdoor enclosure outside to within 5' of the tub. Into the enclosure I hooked up the red to the main the black to the other main and the blue to the neutral bus. I then put in a 2 pole 50A G.F.I breaker hooking the tail from the breaker to the neutral bus in the enclosure. From the tub ran a 6/3 tek cable to the enclosure hooking up the red and black to the breaker but not needing blue (neutral),because there was no neutral connecton in the tub. Is this still effective method of protection?