  • Oct 13, 2009, 01:31 PM
    shartov
    Boiler don't fire up
    Hello all.
    This is an old weil mclain e.g. 75. Pilot is on, but the unit will not start. Changed the thermocoupler and nothing happen. Jumped the 2 wire mercury thermostat and still nothing. A week ago I had electric power problems in the house like short drops lights will dim a bit and came back to full power, computer was shot down and so on. Con Ed came and fix it outside at the pole. Is this problem may have something to do with the boiler? Maybe something went wrong with the control transformer (24 Volts) .
    This is the first attempt to start the boiler after the summer and the pilot light was on all this time (for nothing - last time I'll do that! )
    Any help?
    Thanks in advance, shartov.
  • Oct 13, 2009, 01:33 PM
    hvac1000
    Check for 120 volt power to the boiler
    Then check for 24 volts out of the transformer
    If both of those check out OK then you will have to use your electric meter to back track the circuits till you find the one holding off the boiler.
  • Oct 13, 2009, 02:29 PM
    shartov

    Hi... thanks for the reply... the transformer and boiler has power... no power at the thermostat.
  • Oct 13, 2009, 02:50 PM
    hvac1000
    You are at this point now.

    If both of those check out OK then you will have to use your electric meter to back track the circuits till you find the one holding off the boiler
  • Oct 14, 2009, 05:29 AM
    shartov

    Thanks for the advise... I found the problem at the rollout fuse... boiler is working now. :)
  • Oct 14, 2009, 07:46 AM
    hvac1000
    Good deal and it did not hurt to bad. PS I hope you replaced that very necessary safety device and also located the reason for its failure.
  • Oct 15, 2009, 12:58 PM
    shartov

    Hello there and thanks for the concern... yes, I did replace the ceramic rollout fuse the reason to the problem I found too... last year when I replaced the thermocoupler the supply tube to the pilot broke and local store got me similar but larger tube which with the time leaked gas to the botom... I notice fire on top and botom of the pilot... I guess this extra heat fail the system by breaking the rollout fuse. I change the gas line tube now to the correct size. Wow... thanks again
  • Oct 15, 2009, 01:00 PM
    hvac1000
    I hope your problems are solved.