Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Furnace will not stay lit (https://www.askmehelpdesk.com/showthread.php?t=405337)

  • Oct 12, 2009, 06:02 PM
    wendalfly
    Furnace will not stay lit
    I have a 3 year old concord 80 plus furnace it starts up and ignites for about 10 seconds then shuts off the blower still runs this repeats for about 2-3 more times then just never comes back on again until I restart. I believe it is the round spiral hot surface ignitor what do you think?
  • Oct 12, 2009, 06:12 PM
    hvacservicetech_07

    Sounds like a dirty flame sensor. Sounds like you have located the ignitor, on the opposite side from the ignitor there will be a small silver rod, most likely held in place by one screw, remove sensor and clean with sand paper or wire brush, reinstall and let us know if it works. Be sure to shut furnace off before attempting.
  • Oct 12, 2009, 07:10 PM
    wendalfly

    Did what you said. Sensor was a little dirty. Seems to be working now. Thanks
  • Oct 12, 2009, 08:03 PM
    hvacservicetech_07

    No problem at all. Glad you got it fixed!