    Why does liquid line frost in cooling?
    What would cause a liquid line to frost in cooling?
  • Oct 9, 2009, 07:24 PM
    lyvwyr

    Most commonly would be a dirty filter.
    Low airflow-check blower speed wiring,belt (if applicable),blower wheel
    Low freon
  • Oct 9, 2009, 08:36 PM
    hvacservicetech_07

    Normally a restriction is going to freeze your liquid line, plugged drier,orfice or maybe bad txv.
  • Oct 9, 2009, 09:18 PM
    hvac1000
    A dirty Evaporator coil is the one I dislike the most. Cleaning is a real pain.
  • Oct 13, 2009, 04:57 PM
    hvacpro
    Forgot to mention that this is a heatpump, suction presseure goes to zero, suspect restriction,cant see any obvious signs of damage to line set.
  • Oct 13, 2009, 07:28 PM
    mygirlsdad77

    Does your suction line also freeze? IF suction is reaching zero or below(pulling a vacuum) you most likely have a restriction(as mentioned before, could be filter drier, orafice, txv). You will also see low or vacuum states on suction side if charge is very low. What does your high side read while low side is at zero? And do you notice the high side dropping also when unit is run for a period?
  • Oct 13, 2009, 08:27 PM
    hvac1000
    suction presseure goes to zero

    Check your metering device for restriction (orifice) OR if TXV bad power head..
  • Oct 14, 2009, 03:49 PM
    hvacpro
    High side reads about 150, this was on a cool day about 70 degrees. Did not run the unit very long and the suction line was not cold.