In point of fact Milo. UPC does,indeed, allow wet vents.
908.0 wet venting
UPC code 96 edition
908.1 Wet venting is limited to drainage piping receiving the discharge from the trap arm of one (1) and two (2) fixture unit fixtures that also serves as a vent for not to exceed four (4) fixtures. All wet vented fixtures shall be within the same story; provided, further, that fixtures with a continuous vent discharging into a wet vent shall be within the same story as the wet vented fixtures.
908.2 The piping between any two (2) consecutive inlet levels shall be considered a wet vented section Each wet vented section shall be a minimum waste pipe size of the upper fixture or shall be one (1) pipe size larger than the required minimum pipe size for the sum of the fixture units served by such wet vented section, whichever is larger, but in no case less than two (2) inches.
So there are cases where wet vents are allowed in UPC land. What's next? High loops .on a dishwasher? ( gasp!!). Cheers, Tom