Janitrol GU125-4 won't turn on
Hey all, I've got a ~20 year old furnace that has been running without any issues for the last few years right up until today. Here's my issue. When I set my thermostat to 'heat' and select a temperature, nothing happens. The unit is a standing pilot system, the pilot is lit. I turned everything off and relit the pilot, no change. I can set the fan to 'on' at the thermostat and it fires right up. I have measured voltages at the fan limit switch and here's what I've got. The white line that goes from the transformer -> limit switch -> TH (gas valve) is at 20.8V
The red line on the limit switch is at 120V before turning the fan on, after turning the fan on it drops to 9V and the red line on the other side of the switch then becomes 170V (not sure about this). TR (gas valve) stays at ~1.5V (0V in reference to C on the transformer). It seems to me like I've got a few things happening.
1) The ground between the 120V supply and the thermostat don't seem to be connected. This would explain why TR measures differently when I reference it to different points, is that normal?
2) The gas isn't turning on, that makes me think the gas valve isn't working.
Being that the fan turns on manually, and that the pilot lights and stays lit, I'm inclined to think it's a gas valve problem. Also, I've only owned the house for three years but I noticed today another gas valve sitting next to the furnace. I'm betting its an old one that may have had problems at some other point. Any ideas? Thanks in advance!