  • Oct 1, 2009, 07:14 PM
    Jae30001
    Bryant 395CA Furnace. Code 24.
    I have a Bryant Furnace and I am getting Code 24. 3AMP Fuse is blown. The 120V to 24/40V transformer inside the unit is humming. With a meter I'm getting 20V off a lead, and 28V off another lead. If I disconnect the lead wire from the control board the fuse does not blow. Could this be a bad transformer or am I leading myself in the wrong direction.
  • Oct 1, 2009, 08:01 PM
    hvacservicetech_07

    The fuse that is blown is on the low voltage side which protects the transformer in the case of a short. Disconnect the low voltage wires, install a new fuse, if it blows again you have a bad circuit board if it doesn't, you have a possible low voltage short.