    Oil primary control reset will not reset.
    Oil primary control green light flashing.
    Will not reset due to loss of prime. Just
    Finished cleaning. Changed filter and obviously
    Has to be bled. AFG model Becket burner
    2 years old. How do I get the reset to reset so
    I can bleed the system? All working till now.
    Bruce
  • Sep 30, 2009, 01:32 PM
    wbrucem
    For those not as inquisitive as I. Take the unit off and the answer is on
    A label on the bottom. HOLD DOWN THE RED BUTTON FOR 45 SECONDS.
    AND... BINGO! YOU ARE BACK IN BUSINESS.
    Bruce
  • Sep 30, 2009, 06:36 PM
    NorthernHeat

    Don't repeatedly press the reset botton! Was this oil furnace serviced lately? Nozzels and filters need replaced annually.

    Don't put the fear of God into a potential serviceman and your wife when this furnace begins to walk across the floor because it has too much oil to burn off.