Furnace-Yellow terminal not connected-A/C starts stops
I have a 1988 Rheem RGDA-125-ER furnace. I noticed over the summer that the A/C, when switched to cool, would come on and then immediately switch off if the set temp was higher than the room temp. If I programmed the set temp far below room temp and then switched on, it would run normally and I could then set desired temp and have no problems (would cycle on/off normally). I figured it was the thermostat and would replace later since I could still get it to function. Heat works normally.
Recently I noticed at the furnace that the yellow terminal has nothing connected to it and now I'm wondering if I have a wiring problem.
Current wiring: red from thermostat to furnace red, white from thermostat to furnace white, green from thermostat to furnace green, blue from thermostat to white A/C and blue ("O" or "C") from furnace to red A/C (wire is blue from furnace terminal but marking on furnace terminal is either "O" or "C" - can't really tell).
Your input is really appreciated.
Thanks,
Mike