  • Sep 6, 2009, 02:26 AM
    tahseesinshaa
    127/220v panel schedule
    Hello,
    I am really confused with the panel scheduling of a 127/220V 3 phase 4 wire+G system
    If we use a load of 1000W lighting/220V, we should connect it with 2 phases and is it divides by 500+500 for both phase? Also if a 3 phase load connected, for ex. 6000W/3ph ac-is it to divide by 3.? Can anybody help
  • Sep 6, 2009, 04:23 AM
    tkrussell
    My answers follow your questions:

    If we use a load of 1000W lighting/220V, we should connect it with 2 phases and is it divides by 500+500 for both phase?

    Yes.




    Also if a 3 phase load connected, for ex. 6000W/3ph ac-is it to divide by 3.

    Yes.

    Why is this so confusing?

    Exactly what are you trying to do?