I have A Square D Main panel. It has NO ground bus bar but 3 neutral bars. The neutral and ground wires are both in these bars. Is that O.K.
![]() |
I have A Square D Main panel. It has NO ground bus bar but 3 neutral bars. The neutral and ground wires are both in these bars. Is that O.K.
Is the Main Breaker located in this panel? If so, then the neutrals and equipment grounds can be all connected together.