This should be a straightforward question and answer but so far everyone I've asked has given me the "it's a local code issue" or in my opinion the wrong answer.
I have a 12KW standby generator permanently installed at my home. The ATS is a two-pole transfer with a solid neutral. The generator set is shipped with neutral bonded to ground via a terminal stud on the frame. The instructions say to "lift" the neutral to un-bind it. I've spoken to the distributor of the generator and they said that is the proper procedure. Basically I would connect my main neutral from my ATS to the two neutrals coming from the alternator and tape them off so they do not come in contact with the frame.
I've had the electrician who is helping me tell me that the neutral should stay bonded to ground and the generator equipment ground should be bound to my service ground. Everything else I have read says that since this is NOT a SDS the neutral and ground from my ATS should remain independent so that I only have my N-G bond at the service entrance.
I have four wires from my ATS to generator H-H-N-G and the neutral is NOT switched. The setup my electrician suggests would bond N-G in two places since the neutral is solid.
My AHJ is only part-time in my town (rural area) and it's difficult to get in touch with him other than inspection time.
Thanks