  • Aug 26, 2009, 01:56 PM
    nostalgic_1
    Nordyne furnace pressure switch
    I have a Nordyne M1M furnace that is two and a half years old. A few days ago I turned up the heat on the thermostat and the furnace didn't come on. I looked inside the furnace and the LED light was flashing two times. The legend on the furnace says that two flashes indicate that the pressure switch is open. I bought a new pressure swtich (632453) and replaced it. I'm still getting the same two flashes. Is there anybody there that can tell what the problem may be. PLEASE HELP!! Lee
  • Aug 26, 2009, 04:02 PM
    hvac1000
    It could be the line is plugged up that feeds the switch.
    It could be a defective new switch.
    It could be a defective venter not supplying the switch correctly.
  • Aug 26, 2009, 05:27 PM
    nostalgic_1
    Quote:

    Originally Posted by hvac1000 View Post
    It could be the line is plugged up that feeds the switch.
    It could be a defective new switch.
    It could be a defective venter not supplying the switch correctly.

    Both lines are clear. I can blow through them both. The vent is good. When I disconnect the upper hose from the stack and blow on it the LED stays on constant and the yellow LED comes on and the furnace ignites, but as soon as I quit blowing on it the yellow LED goes out, the flame goes out and the furnace motor quits a while later. When I disconnect the lower hose and suck on it the same thing occurs. Is this then a bad 'new' pressure switch?
  • Aug 27, 2009, 01:16 PM
    nostalgic_1
    I found out that my problem wasn't with my pressure switch (although the LED light was flashing two flashes indicating that there was a problem with the pressure switch). The inducer motor wasn't kicking on first to let the pressure switch work properly. Thanks, though, to hvac1000 for his input to the problem I was having.