1 HP blower motor replace 1/2 HP ?
To make long story short, I have this bad air handler blower problem, a technician came and determined the motor is bad, so he replace old motor with new motor and new capacitor. The unit work for little while then it got overheat and shut down. So we are back to square one, i.e. the blower will run for 10 minutes or so, then shut it off, ice would build up on the evaporator coil.
The tech came and could not figure out the reason; then I notice the replaced motor is rated 1 hp vs the old 1/2 hp, but they both has same 1075 RPM, 230 voltage. Would that cause this problem ?
Old motor: GE 5KCP39PG
New motor: Dayton 3LU92J