  • Aug 20, 2009, 08:05 AM
    hanspelmo
    Inverted zone valve
    Hello,

    I have a 2 zone hydronic controlled by 2 Erie zone valves (model 465B327 30 A1).

    Boiler was replaced from house lately.

    Without power applied to zone valve motor, valve lets water flow pass. (normaly on)

    According to this:

    http://i224.photobucket.com/albums/d...g?t=1241232619

    Normally when thermostat comes on, valve should eventually open and electric contact controlling boiler should come on, right ?


    Mine is reversed. How can I connect these 2 valves to my heating system ?

    Please help !

    Thanks
  • Aug 20, 2009, 03:40 PM
    hvac1000
    The Erie part numbers you provided are incorrect and not listed by Erie. Post correct model numbers.
  • Aug 20, 2009, 04:40 PM
    hanspelmo
    This is what is written on it.

    You can see photo here:

    http://s652.photobucket.com/albums/uu250/hanspelmo/?action=view&current=SDC10152.jpg

    Thanks
  • Aug 20, 2009, 06:42 PM
    hvac1000
    Normally when thermostat comes on, valve should eventually open and electric contact controling boiler should come on, right ?

    Correct as long as the wiring is correct. I have never run into a zone valve that would stay open all the time and only close on a call from the thermostat.

    Usually the thermostat will call for heating and the zone will open allowing the hot water to flow. There is also a end switch that will make during the valve opening to bring the boiler on line.

    You could use relays to reverse control the valves BUT I am not a great believer in engineering a system that way. Best for you to just replace the valves with the proper ones and call it a day.

    The company that replaced the boiler should have taken care of this while they were there.
  • Aug 21, 2009, 07:10 AM
    hanspelmo
    Yes, I though of inverting with relays, but, as you say, it would not be great engineering.

    Just found that :
    A reverse-acting (close-on-rise) thermostat
    Can be used to control a normally open (N.O.)valve.
    http://www.white-rodgers.com/wrdhom/... /0037-6334.pdf

    But it is simpler to change the valve in my case.

    Thank you for the info !
  • Aug 21, 2009, 07:21 AM
    hvac1000
    Overall it will be simpler to change them. Then you have somewhat of a standard system in case you want to do set back thermostata etc.

    What kind of system was originally installed that needed reverse acting valves?
  • Aug 22, 2009, 06:22 AM
    hanspelmo
    Quote:

    Originally Posted by hvac1000 View Post
    Overall it will be simpler to change them. Then you have somewhat of a standard system in case you want to do set back thermostata etc.

    What kind of system was originally installed that needed reverse acting valves?


    It was a gaz boiler, the zone valves were installedd but not operational.

    (Thay were open anyways)