-   -   2 GFI Outlets on same line (https://www.askmehelpdesk.com/showthread.php?t=386786)

  • Aug 14, 2009, 07:44 AM
    TGMcCallie
    2 GFI Outlets on same line
    I have 2 baths which have outlets on the same feeder line. I have one of them protected now with a GFI outlet. Can I add a GFI outlet to the other bathroom
    If so is there any special thing that I need to do with the wiring?

    Thanks
  • Aug 14, 2009, 07:50 AM
    Stratmando

    You can add a regular receptacle in other Bath and hook to Load side of first Bath.
    Or Install Another GFI in the second Bath hooked onto the Line side, so if first Bath GFI trips, it will not trip out second Bath.
  • Aug 14, 2009, 08:44 AM
    TGMcCallie

    I have the other bath hooked to the other receptacle now. If the GFI trips then the other bath receptacle is tripped also. Is that OK as it seems to work but if it trips then I have to go into the bath that has the GFI outlet in order to restore the power.
  • Aug 14, 2009, 09:23 AM
    KISS

    It's fine.

    Can't say it's ideal, but it's fine.

    Two choices for bathrooms:

    1.) The 20 amp circuit may supply bathroom receptacles and lights/fans or other accessories within that bathroom and nowhere else.

    2.) You can supply receptacles in more than one bathroom but only the bathroom receptacles, nothing else can be on the circuit [(NEC 210.11(C)(3)].
  • Aug 14, 2009, 10:08 AM
    TGMcCallie

    Thanks for your help. Right on as usual.
    TG