House wiring and new gen set xfer panel
Thanks for reading this llloooooonnng post! Love to get the same answers more than once!
I want to install a transfer sub-panel for emerg. Back-up from a 5550 gen.
I am finding what I believe are issues with my house wiring, however. Outside I have a 200A main breaker in weather-tite panel that the POCO insisted upon when I built a carport and moved original service weatherhead. The move was just about 4 ft, but around a corner so no wires would be over the carport roof. The meter pan is just beside the outside box (call it Main).
I also have the original 200A panel recessed into a kitchen wall (call it Sub) that is fed from the outside Main and accessed only from inside the house. The service has always been grounded via the meter pan to 1 rod.
Trouble starts here! When I installed the outside box (Main) for exterior access by POCO orders, the inside box became a sub-panel. The Whites (N) and Grounds for all house circuits are together on same Gr bar in sub-panel. Granted, it is only a few feet from the Main and fed by 2' metal conduit (carries Ground back to Main), but I'm told it is improper and N needs to be isolated on new insulated bar on inside panel (Sub). It's a bit crowded in there. I want to install a gen xfer switch sub-panel (call it Xfer Sub) and feed interlocked breakers side-by-side 60A from POCO and 30A from genset. Only one breaker can be on. Gen feed will come in via 4-wire 30A awg10.
Neutral will be floating at gen and gr rod in place for gen frame. 4-wire gen cord w. L14-30 twist-loc ends goes to male pronged inlet box. Box is connected via 4-wire awg 10 to xfer sub panel on wall under carport. The 60 A feed from POCO can come from Sub with a 60A double breaker and 6 critical circuits moved from Sub to Xfer Sub. (water well, refrig, TV, a few lights). I am told that N and Gr must be separated in Sub and only bonded in main.
So questions... no drum roll needed... Once Neutrals are isolated in Sub, do I need a Ground wire from Sub ground bar (where all bare wires are located) back to Main or is 2" metal conduit enough? If so, what size? Or, do I put a ground rod down just for Sub? Or do I tie in to same Ground rod as meter pan 3 ft away? Main has no ground rod connection but meter pan sits just beside it and it is connected to ground rod.
When I feed xfer switch breakers from gen, 2 hots come in on 30A breaker. Do Neutral and ground go to Sub? Re: POCO feed, only two hots #6need enter xfer sub panel from Sub. Load side of breakers splice back into Sub to feed the house wiring that is in place. Thus, current is supplied to those house wires whether from Sub feed (POCO source) or from genset vis 30A breaker. So, two #6s into xfer sub, two #10 into sub feeding bus bar alternately. Six wires leaving Xfer sub from relocated breakers to feed Sub (well and house circuits).
Along with two hot #10 from gen, a neutral pass-thru isolated and tied into neutral bar in Sub as well as bare ground to grounding bar or green screw on box. Since this Xfer sub is in platic flex conduit, a bare gr shall be carried through to ground bar in Sub. I am attching diagram that seems well marked but please check over carefully and critique as needed for Safety. All of this eqpt is so close together but is metal conduit enough of a ground? Thanks so much for your patient review of this.
Equip Grounding Conductor Size
I have a 200A breaker box that used to be a Main and became a Sub panel when an oudoor box was installed ahead of it to "feed-thru" and provide an outside means of disconnect, at the insistence of the Power Company. I have recently learned that this arrangement is not code-compliant since all of the Neutrals and Grounds were on the same bar in what is now the sub-panel and that this must be corrected. I am told that the 3" metal conduit is not an ideal ground connector back to the main since many people do not know how to properly tighten the locknuts where the connection is made and that quality electricians do not rely on that. Since the Sub has a large amp draw potential with all the house breakers in it and the 200A feeds hot, hot and Neutral come into this sub-panel, what size conductor would be appropriate to physically wire the ground back to the main about 4 ft away?