Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Appliances (https://www.askmehelpdesk.com/forumdisplay.php?f=157)
-   -   Rheem Water Heater Gas Kicks Off (https://www.askmehelpdesk.com/showthread.php?t=383313)

  • Aug 4, 2009, 08:36 AM
    hwheat
    Rheem Water Heater Gas Kicks Off
    My heater has a hot surface ignitor.

    Ignitor kicks on - gas kicks on - gas lights - quickly goes out.

    Pulled wires on vacuum switch and put back.

    Works now - ignitor kicks on - gas kicks on - gas lights - quickly goes out - gas kicks back on quickly and stays lit.

    Is something wrong? Do I need to work on it?
  • Oct 1, 2009, 06:58 AM
    hwheat

    I hope this helps someone else with this problem. I finally fixed the problem myself. I called Rheem and they gave me some trouble shooting tips. Check the vacuum switch - which was fine. If not vacuum switch, likely the controller.

    I actually replaced the controller and the problem went away for a few days then came back.

    After exhaustive troubleshooting, I found a slightly open male terminal on the lead from the 24V transformer that connects to the gas valve. I was getting 24 volts, but the valve was not working. I reduced the gap with a pair of needle nose pliers and the problem is fixed.

    I reinstalled the original controller and found that it was actually faulty. It would provide 24 volts for about 1 second then go to zero. So - I had two issues.

    Again - I hope this helps someone else.