Shed and generator wiring
I have read a good deal and appreciate the help. I still have a couple of things that need clarity.
Details: I have an outside breaker box just beside the meter pan with 200A mains for 120/240 VAC 200 A service. There are 8 spaces available and two are currently filled with a shed breaker, a double 30A. This was added 23 yrs ago at the insistence of the power company since my original service panel had the mains in it inside the house. I wanted to add a carport and was told that the service entrance had to be moved since the incoming service could not be over a roof. Luckily, the service was on the N side of the house near the corner and had to be moved just around the corner to the W side, only about a 5 ft move. I chose to bring the service from the nearest pole underground. It was previously overhead. So far - POCO to underground wiring - up to panel with mains and 8 spaces for miscellaneous breakers - around the corner through metal conduit to inside panel with , again 200A mains and forty spaces GE 200A panel from 28 yrs ago.
Q1) shed wiring - The outbuilding is about 50 ft from the house and was reached with 10-2 with Ground direct burial cable. From a double 30A breaker in the outside breaker box. The problem there is that it is attached to a double 30A breaker in the outside breaker box essentially picking up 120V on each of the white and black leads. (My 240V water well is wired the same way on a 10-2 + bare Gr). The two hot leads supply a sub panel in the shed and are split into 2 separate 120V circuits. I have no equipment in the shed requiring 240V. Table saw router etc all run on less than 20A and 120V. SO... should the shed sub-panel be rewired (both ends) from a single 30A breaker in the house outside breaker box employing the buried cable 10-2 w Gr and have one 30A 120V circuit in the shed? I believe that I should get a sub panel for the shed that does not "bond" neutral to ground and that an additional ground rod at the shed is acceptable but not necessary. Is such a sub-panel available where GR and white neutral are kept separate?
Q2.) The water well is self grounding is it not? So is the 3-wire cord going 50 ft to the water well OK?
Q3) What started me investigating the whole thing is the need to hook up a gen set to the house for emergency b/u. I really need the water well and a few other things (the frig)are luxury. After Katrina we were able to get one TV station via satellite and it was great to know what was happening. We were without POCO for 2 weeks and I live about 80 mi from Ground zero. I have a 5550 watt gen set with 8700 surge watts. The inside breaker box is recessed into the wall and full so I believe the outside breaker box is the likely candidate for an Interlock Kit. I have read about removing the bonded neutral and floating it on the gen set and have instructions for my particular gen. It should be easy and I will ideally toggle it and mark the positions. I want to use a power cord to reach 20 ft to a power inlet and believe 10 AWG is enough. (Q3-A) Is a 10-3 w Gr required here ? Or is 10-2 w Gr OK. (Q3-B) Is it safe to use a grounding rod (already in place beside where gen sits). From the inlet box to the outside breaker box where Interlock Kit will install, it is about 30 ft and I have some 8-2 w gr solid wire. (Q3C) Do I need a 4th wire to serve as insulated neutral or ground and if so, would a single insulated awg 10 be adequate since I'm on a 30A circuit? Is it necessary to run a Ground if gen frame is tied to rod as is the main panel?
This is all less than ideal but with inside breaker box recessed near a kitchen corner, I do not want a surface mount transfer panel and even less want to start tearing out sheetrock below the panel to drill holes in the bottom plate for more wire. It is a raised house so the possibility is there. The outside breaker box is exposed to weather so the Interlock Kit seems ideal.
Thanks, curlie.
shed and generator - follow-up
It was a lengthy description but got an answer instead of questions for more info needed. Thanks, TK. -
RE: Shed: I did mention the shed had a sub-panel with two 20A 120V circuits; I did not mention that two 20A breakers are in place in that panel, one for each circuit. I will convert the shed to one circuit, Bl = hot W = Insulated Neut and Bare = Eqt Gr. Neut and Gr will be kept separate by installing another strip in sub-panel and keep grounding clamp to rod in place at shed. Thanks for confirmation on all .
Re: The Gen will hook to a power inlet box via a 25ft cord and male inlet type L14-30. The inlet box will hook to wiring that must travel 30 ft before reaching a backfeed breaker. I have 35 ft of 8-2 w bare Ground (solid) that was given to me. The extra strand of wire that I think I need will run along with the 8-2. I suppose the best thing to buy is a single strand of RED since the 8-2 contains BL & W. I intend for these wires to carry 2 hots Bl and R along with a Neut Wh along with Bare Ground from the 4-wire power inlet to the backfeed breaker, some 30 ft. Since I already have the 8-2 w Gr all I might need is a single cable capable of carrying 30A since the gen plug (output), the inlet power receptacle, and the backfeed breaker are all rated for 30A. The questions are will the size 8 conductors fit into the L14-30 device (gen power inlet) and will the extra Red conductor need to be the same size as the 8-2 conductors? Theoretically, #10 should carry the load, but I am using #8 since I have it.
Thanks, curlie jones