-   -   Thermostat wiring-- Where does the blue wire go? Its HOT out! (https://www.askmehelpdesk.com/showthread.php?t=380963)

  • Jul 28, 2009, 07:27 PM
    rutterback
    Thermostat wiring-- Where does the blue wire go? Its HOT out!
    I bought a Honeywell rth221b thermostat. I was smart enough NOT to mark the wires when I took off the old one.:mad: the wires that come out of the wall are red, green, white, and blue. The thermostat looks like this-

    Y-o o-Rh
    G-o o-Rc
    o-W

    Im assuming green to G, red to Rh (Rh and Rc have a jumper between) and white to W. Where in the world does blue go?? My heat worked but not my central air. Im assuming the A/C is the blue wire?

    Like a typical guy, I threw away the instructions months ago and never checked to see if the AC worked... Smart... I know.

    Thank you in advance for your help and tips.
  • Jul 28, 2009, 07:38 PM
    KISS

    Blue has to be (Outside unit - Y) especially if manual fan works because that is G. In AC mode the thermostat controls the fan.
  • Jul 28, 2009, 08:00 PM
    ballengerb1

    You might want to print this out after reviewing it. https://www.askmehelpdesk.com/heatin...eat-58313.html I am thinking blue to yellow but read the whole thread.
  • Jul 29, 2009, 06:03 AM
    dac122

    I also say blue wire to Y terminal. Here are your instructions.
  • Jul 29, 2009, 02:32 PM
    rutterback
    1 Attachment(s)
    THANKS for the answers! Almost there!

    This is what's on my furnace. How do I know if my AC unit has a transformer? I don't know if I should use the jumper.

    Hope this is helpful!
  • Jul 29, 2009, 02:35 PM
    siberianair

    Need a jumper between rh and rc... blue goes to y terminal...
  • Jul 29, 2009, 02:36 PM
    ballengerb1

    This looks bit odd to me. I see the blue wire going to the yellow terminatal but I also see another red going to the same terminal. I think it goes to the one vacant terminal marked G, what do you think KISS?
  • Jul 29, 2009, 04:17 PM
    wmproop
    Looks to me like the whitish-yellow and the red are the ones used to go outside to the ac unit,, this is OK rutterback
  • Jul 29, 2009, 06:56 PM
    rutterback
    1 Attachment(s)
    Nothing is working... this is what my thermostat looks like... thanks again for everyone's patience.
  • Jul 29, 2009, 07:13 PM
    rutterback
    Which one should I try in the "G"?

    Thank you
  • Jul 29, 2009, 07:20 PM
    ballengerb1

    Move the red off the yellow leaving the blue still connected to yellow. Move red to the empty G on the right.
  • Jul 29, 2009, 09:34 PM
    KISS

    I think we need to start completely over. This looks way to simple and it should be working. Hah.

    I propose - disconnect the thermostat.

    We are going to "play thermostat". So before trying things disconnect power. Can I assume that you don't have a voltmeter? Leave the wires attached because they are disconnected at the other end. Just add the jumpers.

    Jump R to Y and Gc at the furnace. Turn on furnace. Outside unit and fan should come on. Might have to wait 2-5 minutes. Fan will come on immediately.

    Turn off power. Remove these jumpers.

    Jump R to W. Turn on power. Furnace should comeon and a short time later, the furnace fan should come on.

    Turn off furnace. Remove jumpers.

    That checks out the furnace.

    DO the tests and report back.
  • Jul 30, 2009, 03:55 AM
    siberianair

    Check the fuse near your circuit board or maybe you blew the transformer.
    You did turn the power off before playing with wires on tstat didn't you?
  • Aug 12, 2009, 12:58 PM
    rutterback

    Nothing is working! Please help!! Its 95 outside!
  • Aug 12, 2009, 01:04 PM
    rutterback

    I never shut the power off like an idiot. I don't know if there is a voltmeter either? I'm going to try what KISS said... ill report back.. thank you
  • Aug 12, 2009, 01:40 PM
    ballengerb1

    I never did understand siberairs comment and reddie to me. He said I was wrong but never explained further. I have not seen a board on the furnace with 2 wires going to it. The blue/yellow sends the signal, the second red should be jumpered at the stat.
  • Aug 13, 2009, 05:09 PM
    ballengerb1

    This may amuse you but I see that Siberianair has been blocked out as a troll. Maybe skip his suggestions for now.
  • Jun 7, 2011, 04:03 AM
    Smackcat73
    Rutterback--- what did you ever do to solve the problem? I'm having the same issue!