    rswank
    LED on Trane XB90 not on
    I have an Trane XB90 furnace and just recently moved the thermostat up a bit on the wall to make room for a light switch. I didn't cut power first and think I touched the stat wires. After hooking the stat back up the furnace would not turn on. I recycled power to the furnace and that did not help. Also, the red LED is NOT on at all on the board. I am thinking the board is fried. If I have power to the furnace and the led is not on at all would there be any other explanation other than a bad board?
  • Oct 18, 2006, 03:40 PM
    NorthernHeat
    Quote:

    Originally Posted by rswank
    I have an Trane XB90 furnace and just recently moved the thermostat up a bit on the wall to make room for a light switch. I didn't cut power first and think I touched the stat wires. After hooking the stat back up the furnace would not turn on. I recycled power to the furnace and that did not help. Also, the red LED is NOT on at all on the board. I am thinking the board is fried. If I have power to the furnace and the led is not on at all would there be any other explanation other than a bad board?

    It is more likely a fuse in the low voltage cicuit in the furnace The fuse can be inline, or on the board. It is also possible you burnt out to transformer.
  • Oct 19, 2006, 06:36 AM
    rswank
    Quote:

    Originally Posted by NorthernHeat
    It is more likely a fuse in the low voltage cicuit in the furnace The fuse can be inline, or on the board. It is also possible you burnt out to transformer.

    Yep it was a 3amp fuse.
    Thanks!