Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   How many amps required for split system (https://www.askmehelpdesk.com/showthread.php?t=377572)

  • Jul 19, 2009, 11:13 PM
    JUNEZ
    How many amps required for split system
    We need to install a heating/cooling split system inverter (8.0w/9.0w by memory).
    We have an exsiting 16amp isolator for the a/c unit and the label on the unit says heating/cooling requires 11amp. However the instruction manual says 30amp fuse is required.
    We've spoken to 2 electricians, one says that the 16amp fuse is sufficient while the other one says that we need more.

    Any suggestions.. Thanks!
  • Jul 20, 2009, 12:03 AM
    hvac1000
    You go by circuit ampacity for the device or unit you are wiring. If it calls for a 30 amp circuit then usually number 10 copper and a 30 amp breaker along with a proper size inverter for the unit.