Do I need another HVAC return?
I live in a 2-story 2500 sq. ft. house with 2 split R-22 units that are over 8 years old. The downstairs 2-1/2 ton cools (and cycles) fine. The upstairs is a 3-1/2 ton unit for approx 1350 sq ft. The upstairs runs all day long here in Houston. Here are some specifics
Outside Temp: 90deg
WB temp at return: 65
Dry bulb temp at register: 75
temp at first register after evap: 61
Temp of suction line just before service valve: 54
Low pressure gauge reads: 75 corresponding temp-43
High pressure liquid line reads: 260
Return air grill is 20x30 and I use the Filtrete Ultra (Purple) filters, and always have.
my unit will only cool to 78-79 in heat of the day.
Will installing another 20x30 return help this problem? The return air rectangular duct that runs into the furnace is approx 12x16. I would be tying into this with another 16-inch return flex duct.