Running electrical sub panel to pole barn.Does this require 3 conductor service entrance wire with ground ( 2-2-2-4 ser)? Or 2-2-2 seu ?
![]() |
Running electrical sub panel to pole barn.Does this require 3 conductor service entrance wire with ground ( 2-2-2-4 ser)? Or 2-2-2 seu ?
Need 4 wire, plus the neutral and ground need to be separated at the new panel ,and at least one ground rod needs to be driven and connect to the equipment ground bar.