  • Jun 27, 2009, 06:22 AM
    Troubled boy
    A/C running but not cooling
    My A/C fan is blowing but not cool air come out, I can feel the air blow out as normal. Here is what I have checked - 1)outside unit has power, the fan is running, the air blow out is NOT warm, the two pipe out of the unit going to the room is regular tempture. 2)inside unit has power, the drainning water tray is empty, the drainning pipe going outside is working, I tested with pour in water, and I saw water came out of the outside house. The two pipe are same tempture, it does look like work at all. The filter is new.

    What that could be? Do I need call for service? Many thanks
  • Jun 27, 2009, 03:17 PM
    hvac1000
    Sounds like the compressor in the outside unit is not working. It could be a burnt wire or a frelay or capacitor if so equipped.

    If you do not have the test equipment or tools and the knowledge in how to use them then you better call for on site service.
  • Jun 27, 2009, 09:22 PM
    Troubled boy
    Thank you very much for your reply.
    Can I see the burned wire or capacitor from the outdoor unit? I hope is not compressor, this unit is only 6 years old. Thanks
  • Jun 28, 2009, 02:30 AM
    hvac1000
    The burnt wiring or defective capacitor will be in the service compartment behind the access door.
  • Jun 29, 2009, 04:17 PM
    Troubled boy

    You are the man, the capacitor did the trick. Many many thanks to you.
  • Jun 29, 2009, 05:33 PM
    hvac1000
    Glad it all worked out for you. Keep cool.