Originally Posted by
tkrussell
Do not pull NM thru exterior conduit, not allowed as NM is rated for dry locations only.
Pulling NM, esp #6-3, is not done other than a short sleeve thru walls or for protection. Conduit needs to be grossly oversized to handle NM cable.
PVC Sch 40 is fine. Need to check local codes as many require steel as PVC rises out of concrete.
Not sure where Stan came up with 4 inch covering over conduit. Table 300.5 of the NEC allows a min of 2 inch,althou deeper is better.
You could do this run entirely in PVC Sch 40, even where exposed under th eave.
Horizontal runs of PVC need added straps, as PVC sags. Long runs, esp when exposed to sunlight, need expansion couplings, as PVC expands and contracts greatly.